Hi all,
I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap price. It was cheap because its batteries were near the end of their life. Replacing the batteries with the same kind of dry cell lead acid is prohibitively expensive here. I was thinking I would replace them with ordinary wet cell automotive batteries because they are really cheap. These wet batteries are not the maintenance-free type and they won't obviously fit in the casing. I will have to keep them watered but that's ok by me. My concerns are: is there a charging cycle difference between the two types of batteries? Will the charger in the UPS work OK? Any danger of batteries getting burnt or exploding? I did some search on Google and I could only learn that UPS batteries are deep cycle while automotive batteries are not. Will that have any negative effect on the UPS? Any help is appreciated. -Hasan. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
Hasan A. Khan wrote:
> I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap > price. It was cheap because its batteries were near the end of their > life. Replacing the batteries with the same kind of dry cell lead acid > is prohibitively expensive here. I was thinking I would replace them > with ordinary wet cell automotive batteries because they are really > cheap. These wet batteries are not the maintenance-free type and they > won't obviously fit in the casing. I will have to keep them watered but > that's ok by me. > > My concerns are: is there a charging cycle difference between the two > types of batteries? Will the charger in the UPS work OK? Any danger of > batteries getting burnt or exploding? I did some search on Google and I > could only learn that UPS batteries are deep cycle while automotive > batteries are not. Will that have any negative effect on the UPS? Any > help is appreciated. Hi Hasan, Sealed lead-acid batteries are more fussy than liquid electrolyte types. So I think you should have no problem electrically using wet cells. Automotive batteries can take fewer deep discharge cycles, but unless you frequently run the UPS flat I see no problem with lifespan. But please be aware that if you mount the batteries externally, unsafe voltage will probably be on one or both of the terminals, 240 volts is quite possibly connected to one terminal depending on where ground is referenced. Being "wet" cells the surface of the batteries may also have high voltage that can cause accellerated corrosion to anything they are in contact with. Putting them in battery boxes is a good idea. Or at least "non flammable" picnic coolers or plastic storage tubs. :) Cheerful regards, Bob -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
Hasan A. Khan wrote:
> I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap > price. It was cheap because its batteries were near the end of their > life. Replacing the batteries with the same kind of dry cell lead > acid is prohibitively expensive here. I also got a APC UPS for dirt cheap ($0) with a dead battery. It turns out APC has a battery swap program. For a few 10s of $$ they sent me a new battery and a prepaid UPS label to send back the old battery. I don't remember the battery specs and the exact price, but do remember thinking the price was fair at the time. That was a year or so ago, and the UPS has been working fine and rode out a few power glitches since then just fine. > I was thinking I would replace > them with ordinary wet cell automotive batteries because they are > really cheap. In my case a car battery would have cost more. The real problem with car batteries though is that they are not intended to be deeply discharged. They are optimized for high current delivery for a short time as apposed to capacity and the ability to recover from deep discharge. ******************************************************************** Embed Inc, Littleton Massachusetts, http://www.embedinc.com/products (978) 742-9014. Gold level PIC consultants since 2000. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
>In my case a car battery would have cost more. The real problem with car >batteries though is that they are not intended to be deeply discharged. >They are optimized for high current delivery for a short time as apposed to >capacity and the ability to recover from deep discharge. You would need to get a "Deep Cycle" Wet Cell Lead Acid battery. These are often referred to as "Marine" or "RV" batteries as well. They are designed to be discharged down much further than auto starting batteries without serious damage to the battery. Regards, Kevin Jones -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
As well, you will get a LOT more running time when the power fails.
Conversely, it will take a lot longer to recharge them when the power comes back on, since the charger is probably designed to put out current appropriate for the existing batteries. But since (hopefully!) the time between power failures is relatively long, this shouldn't matter. Larry Original Message: You would need to get a "Deep Cycle" Wet Cell Lead Acid battery. These are often referred to as "Marine" or "RV" batteries as well. They are designed to be discharged down much further than auto starting batteries without serious damage to the battery. Regards, Kevin Jones -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
At 01:14 PM 4/30/2009, Hasan A. Khan wrote:
>Hi all, > >I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap >price. I was thinking I would replace them with ordinary wet cell >automotive batteries because they are really >cheap. Couple of things: 1) Should work just fine in terms of charging. Gel-cells are WAY more fussy than flooded batteries about charge techniques. 2) Modern automotive batteries aren't designed for frequent deep-discharge cycles. They will tolerate some deep discharge operation but not as often as RV or marine batteries. That said: how often do you expect the batteries to operate until they are dead? If that's not often, then no problem. Occasional testing is definitely NOT a problem. 3) Make sure the battery terminals can't be touched. There is a significant chance that the batteries are connected directly to the incoming power line. Plastic battery cases with lids would help there, along with appropriate warning labels. Keep in mind that you are trying to protect people other than yourself from harm. 4) Try to get batteries with removable vent caps - both so that you can keep the battery filled as well as for hydrometer testing. Purchase a battery hydrometer and learn how to read and interpret it. Mark the hydrometer reading on the battery when it is new and fully-charged so that you have something to compare to in a few years time. Go for it! I suspect that you will be quite happy with the results. dwayne -- Dwayne Reid <[hidden email]> Trinity Electronics Systems Ltd Edmonton, AB, CANADA (780) 489-3199 voice (780) 487-6397 fax www.trinity-electronics.com Custom Electronics Design and Manufacturing -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
On Fri, 2009-05-01 at 00:14 +0500, Hasan A. Khan wrote:
> Hi all, > > I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap > price. It was cheap because its batteries were near the end of their > life. Replacing the batteries with the same kind of dry cell lead acid > is prohibitively expensive here. I was thinking I would replace them > with ordinary wet cell automotive batteries because they are really > cheap. These wet batteries are not the maintenance-free type and they > won't obviously fit in the casing. I will have to keep them watered but > that's ok by me. Frankly, it's been a while since I've seen a car battery that wasn't maintenance free. Adding water? That's a long time ago. You're main problem is regular automotive batteries are designed to always be at the top of charge and deliver short bursts of many amps. They are called "starting batteries" and are completely the wrong type of battery to connect to a UPS. What you need a "deep cycle" batteries. They are more expensive, but are designed for the kind of load a UPS is. > My concerns are: is there a charging cycle difference between the two > types of batteries? Will the charger in the UPS work OK? Any danger of > batteries getting burnt or exploding? Lead acid charge cycles are pretty much the same across the board, pretty much any lead acid charger will work with a lead acid battery, as long as the charged isn't designed for a LARGER battery then you plant to use. Make sure you match the capacities of the replacement batteries. > I did some search on Google and I > could only learn that UPS batteries are deep cycle while automotive > batteries are not. Will that have any negative effect on the UPS? Any > help is appreciated. Don't even bother using non deep cycle batteries. Just a few cycles and their capacity will be so destroyed as to be almost unusable. TTYL -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
Herbert Graf wrote:
> On Fri, 2009-05-01 at 00:14 +0500, Hasan A. Khan wrote: >> Hi all, >> >> I recently purchased a used APC SmartUPS 2200VA UPS at a dirt cheap >> price. It was cheap because its batteries were near the end of their >> life. Replacing the batteries with the same kind of dry cell lead acid >> is prohibitively expensive here. I was thinking I would replace them >> with ordinary wet cell automotive batteries because they are really >> cheap. These wet batteries are not the maintenance-free type and they >> won't obviously fit in the casing. I will have to keep them watered but >> that's ok by me. > > Frankly, it's been a while since I've seen a car battery that wasn't > maintenance free. Adding water? That's a long time ago. Actually if you look at most of them carefully the cheaper (non-AGM style) "Maintenance Free" batteries, the little cell covers come right off on top, and lo-and-behold, there's the good old fashioned battery -- same tech it always was. The only difference is the seals have gotten better, so less water evaporates. I've found "maintenance free" batteries that needed distilled water badly, came right back to life when "maintained". Go figure. > What you need a "deep cycle" batteries. They are more expensive, but are > designed for the kind of load a UPS is. Like these... http://www.cdstandbypower.com/product/battery/vrla/pdf/12_310.pdf I got lucky and got four of these from a site that was required to "decommission" them every couple of years, whether they needed to or not. Many critical big rack-mounted UPS systems are required to replace their batteries on a schedule, no matter their condition. These were fine. Nate -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
On Thu, Apr 30, 2009 at 11:38 PM, Nate Duehr <[hidden email]> wrote:
> > Actually if you look at most of them carefully the cheaper (non-AGM > style) "Maintenance Free" batteries, the little cell covers come right > off on top, and lo-and-behold, there's the good old fashioned battery -- > same tech it always was. The only difference is the seals have gotten > better, so less water evaporates. I've found "maintenance free" > batteries that needed distilled water badly, came right back to life > when "maintained". Go figure. > Hmmm. Water doesn't leak out through evaporation or seepage - it is lost when the battery is charged, which inevitably results in some water being turned into H2 and O2. In a sealed lead acid battery, there has to be some material to hold the electrolyte slightly "away" from the plates so that the O2 can reach them to recombine (either a gelled electrolyte or a glass mat - anything which will allow gaseous diffusion between the plates and the airspace above them). This takes some hydrogen from the acid and combines it with the O2 to make water again (at the expense of slightly weakening the acid). The H2 can diffuse right through the plastic case so it does not recombine. This is still better than letting the battery dry out. So, as far as I know, there is no such thing as a flooded lead acid battery which does not need to have water added. I suppose that you could prevent the user from adding water, but then a perfectly good battery would be wasted. The amount of water loss is greatly reduced if you do not overcharge the battery, since most of the hydrolysis of water happens at the very end of the charge. It could be that modern cars control the charge voltage better so that there is significantly less hydrolysis. Note that no lead acid battery can be completely sealed. The gel cells and AGM batteries have little one-way valve vents which open when the internal pressure reaches a certain point. They close again when the pressure goes back down. This is needed as a safety mechanism as it is normal for the pressure to rise inside the battery. You can even hear these "squeal" a bit when a sealed lead acid battery is overcharged - which is actually somewhat necessary to equalize the cells and reverse sulfation of the plates. Sean -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Dwayne Reid
>3) Make sure the battery terminals can't be touched. There is a
>significant chance that the batteries are connected directly to >the incoming power line. Plastic battery cases with lids would >help there, along with appropriate warning labels. Keep in mind >that you are trying to protect people other than yourself from harm. And to protect yourself from harm while checking the batteries, go down to your local auto wrecker and see if you can get enough of the little plastic terminal covers that get put on the 'hot' battery terminal when they are in a car. These will protect you from touching the terminals accidently, or inadvertently shorting across a battery with something metal, while checking the electrolyte. The battery supplier may also be able to supply these as well, or supply them from old batteries. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
Most UPS manufacturers, APC included, ensure that the batteries
are not labeled with the voltage or amp-hour rating because they want you to buy their battery packs. If you measure the existing batteries, you can compare dimensions & known values to catalog data to figure out what third party batteries are exact matches. > You would need to get a "Deep Cycle" Wet Cell Lead Acid battery. > These are often referred to as "Marine" or "RV" batteries as well. Most of the UPSes that I've worked on use multiple 7 to 12 amp-hour batteries to form battery packs. Most car batteries are 25-35 amp-hour. Large truck batteries may be have even higher amp-hour ratings. If you make a battery pack from wet cell car batteries, what the original UPS battery pack saw as a deep discharge (for a given load for specific time) is a much less deep discharge of the car batteries. Most power outages (in the US) are only a minute or two, so the UPS won't deeply discharge either a dry (sealed) or a wet cell pack if the batteries are in decent condition. Lee Jones -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
On Fri, 1 May 2009 02:37:27 -0700, Lee Jones wrote:
> Most UPS manufacturers, APC included, ensure that the batteries > are not labeled with the voltage or amp-hour rating because they > want you to buy their battery packs. If you measure the existing > batteries, you can compare dimensions & known values to catalog > data to figure out what third party batteries are exact matches. > > > You would need to get a "Deep Cycle" Wet Cell Lead Acid battery. > > These are often referred to as "Marine" or "RV" batteries as well. > > Most of the UPSes that I've worked on use multiple 7 to 12 amp-hour > batteries to form battery packs. I've done some experimenting with UPSs and their batteries - the ones they supply aren't Deep Cycle, they're designed (and often labelled) "for standby use" which means they expect to be kept topped-up, and not discharged very often. By discharging a bank of UPS batteries until the UPS shuts down and recharging them immediately, once a day, I found that the time they'd run would start to deteriorate after about ten or a dozen cycles. Starting at about 4 hours' endurance, after a month it was down to about 2.5, and dropped by a few minutes each day. After three months it was less than an hour, and I stopped at that point. > Most car batteries are 25-35 amp-hour. Large truck batteries may > be have even higher amp-hour ratings. Indeed, but they're not designed for Deep Cycle either - they're designed to start the engine and then be immediately recharged. Back in the good old days when cars were fitted with ammeters, you could see when the battery was "full" because the ammeter read zero while the engine was running. A single start takes only about a quarter of an hour to recover, but if you have starting problems and almost flatten the battery, it would take three or four days' normal journeys before it was "full". > If you make a battery pack from wet cell car batteries, what the > original UPS battery pack saw as a deep discharge (for a given > load for specific time) is a much less deep discharge of the car > batteries. Most power outages (in the US) are only a minute or > two, so the UPS won't deeply discharge either a dry (sealed) or > a wet cell pack if the batteries are in decent condition. Proper Deep Cycle batteries have much heavier plates than any other type, so they tend to be bigger and heavier for a given capacity - and also much more expensive. As you say, the bigger the battery capacity the better, because for a given amount of energy extracted it will be discharged less deeply. As for how long a power cut lasts - the record here was 17 hours! It has to be said that was the longest by far in the 25 years I've been living here - a tree came down in a storm and took down the HV lines *and* blew the transformer (the next longest was 8 hours, then about 2.5). You can't expect to use UPSs for this, so that's when I broke out the generator. Cheers, Howard Winter St.Albans, England -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Nate Duehr
On Thu, Apr 30, 2009 at 11:38:28PM -0400, Nate Duehr wrote:
> Herbert Graf wrote: > > On Fri, 2009-05-01 at 00:14 +0500, Hasan A. Khan wrote: > >> Hi all, > > What you need a "deep cycle" batteries. They are more expensive, but are > > designed for the kind of load a UPS is. > > Like these... > > http://www.cdstandbypower.com/product/battery/vrla/pdf/12_310.pdf > > I got lucky and got four of these from a site that was required to > "decommission" them every couple of years, whether they needed to or > not. Many critical big rack-mounted UPS systems are required to replace > their batteries on a schedule, no matter their condition. These were fine. Nate, Can you define "fine"? I have access to used batteries of that exact model and manufacturer. I'd like to use them for my electric car that I'm trying to put together. Have you done any controlled charging/deep discharge cycling as described elsewhere in this thread? If so how did they hold up? I'm probably going to pull the trigger on them anyway because I can get a full double bank for less than $500. But it would be good to know how well they function in a moderate to deep discharge cycle application. BAJ -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Herbert Graf-5
"Herbert Graf" <[hidden email]> wrote in message news:1241128232.6224.15.camel@not-the-one... > Frankly, it's been a while since I've seen a car battery that wasn't > maintenance free. Adding water? That's a long time ago. Funny, the batteries in two of my three cars let you add water. Also, in the past, I've had a few "maintenance free" batteries where you could still pry the tops off and add water. Those were weird. > Don't even bother using non deep cycle batteries. Just a few cycles and > their capacity will be so destroyed as to be almost unusable. Agreed. Plus the deep cycle battery I've got at home (battery powered backup sump pump) has screw on caps to add water. It's about the size of a car battery and wasn't terribly expensive (maybe $60 a few years ago). Jeff -- "Take heart amid the deepening gloom that your dog is finally getting enough cheese" - Deteriorata - National Lampoon -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Howard Winter
On Fri, 2009-05-01 at 11:44 +0100, Howard Winter wrote:
> By discharging a bank of UPS batteries until the UPS shuts down and recharging them immediately, once a day, I found that the time they'd run would start to > deteriorate after about ten or a dozen cycles. Starting at about 4 hours' endurance, after a month it was down to about 2.5, and dropped by a few minutes each > day. After three months it was less than an hour, and I stopped at that point. Wow, that's kinda surprising, thanks for running that experiment! I thought the batteries in UPSs were deep cycle. It's reassuring though to read that your results matched what I've read in the past (that "starting" batteries are significantly effected capacity wise after only 10 deep cycles, vs. the 100+ of real deep cycle batteries). TTYL -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Byron Jeff
On Fri, 1 May 2009 07:08:18 -0400, "Byron Jeff" <[hidden email]> said: > On Thu, Apr 30, 2009 at 11:38:28PM -0400, Nate Duehr wrote: > > Herbert Graf wrote: > > > On Fri, 2009-05-01 at 00:14 +0500, Hasan A. Khan wrote: > > >> Hi all, > > > What you need a "deep cycle" batteries. They are more expensive, but are > > > designed for the kind of load a UPS is. > > > > Like these... > > > > http://www.cdstandbypower.com/product/battery/vrla/pdf/12_310.pdf > > > > I got lucky and got four of these from a site that was required to > > "decommission" them every couple of years, whether they needed to or > > not. Many critical big rack-mounted UPS systems are required to replace > > their batteries on a schedule, no matter their condition. These were fine. > > Nate, > > Can you define "fine"? I have access to used batteries of that exact > model > and manufacturer. I'd like to use them for my electric car that I'm > trying > to put together. > > Have you done any controlled charging/deep discharge cycling as described > elsewhere in this thread? If so how did they hold up? > > I'm probably going to pull the trigger on them anyway because I can get a > full double bank for less than $500. But it would be good to know how > well > they function in a moderate to deep discharge cycle application. Sorry, not yet. They've been on one of those little "four cycle" 1A lead-acid chargers that are commercially available for a few years, and only get used during power outages. The "stuff" hooked to them is connected through a powerpole distribution block that has a low voltage cutoff that is set for around 10VDC, and it's never tripped. (They power the ham shack. Slowly moving to having everything including the PC on 12VDC, but it's not a high priority for me right now, since I'm not home enough to really enjoy the ham shack right now... nor is the three year old tower project even started yet. LOL!) I probably *should* run some tests to see how long the four of them would last and to make sure they're still matched, but haven't done it yet. A local group has also been using them for Field Day activities for as long as I've had mine, and they're not reporting any loss of capacity yet (three years). They "abuse" them more than I do mine. They use them once a year, store them, charge them maybe twice a year... They seem pretty "tough". But no, I can't quantify that in any real "engineering" way. Sorry. I was just using them as an example of a very high capacity lead-acid supposedly *designed* for UPS/high-current/deep-cycle duty, vs. say a standard car battery. Another local friend loves his AGM "Yellow Top" Optima batteries since they're supposed to be somewhere between "deep cycle" and "starting battery", but I've had a "Red Top" fail in a rather concerning way in my Jeep (it bulged badly while just using it for normal staring duties, and the rest of the system checked out fine) and I won't use them anymore. I was an outspoken fan of them too, right up until my starting battery gained a couple of inches of height! Not cool. (That leads to a completely unrelated story, but I love Sears. I started with a "4x4" battery, it failed early, paid a slight difference in price on warranty to "upgrade" to the Red Top, and it bulged, and they replaced it again, free of charge. They've been great about replacing batteries that are dying before their time. With no electrical problems, I suspect the high vibration environment of "real" 4X4 roads on a regular basis is the root-cause reason these batteries are dying.) Nate -- Nate Duehr [hidden email] -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
Thanks for everyone for their help!
My main concern was if the UPS's would work fine with wet cell batteries and according to you guys, it will. So I am mostly happy. The concern about deep cycle issues is still there since the batteries will be discharged to about 80% of full charge atleast twice a weak. Given that the batteries are well taken care of otherwise, will they last two years with that frequency of deep discharge? Also I was not aware of the fact that 220V can appear on the battery terminals. I don't understand how that can happen. I'd like to look at some basic UPS circuits that will show it. Any pointers welcome. I thought some sine/square wave is pumped into a step-up transformer with input and output being isolated by the transformer. So how does high voltage appear at the battery terminals? Thanks again. -Hasan -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
Hasan A. Khan wrote:
> The concern > about deep cycle issues is still there since the batteries will be > discharged to about 80% of full charge atleast twice a weak. Given that > the batteries are well taken care of otherwise, will they last two years > with that frequency of deep discharge? This has already been abundantly answered. It seems the only issue is you don't like the answer. ******************************************************************** Embed Inc, Littleton Massachusetts, http://www.embedinc.com/products (978) 742-9014. Gold level PIC consultants since 2000. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
Hasan -
Auto starter batteries in your app are unlikely to last more than a few months. If that's what's available I suggest adding batteries in parallel to increase the A/H capacity. Starter batteries discharged below 15-20% capacity will have short and unhappy lives. Adding batteries in parallel is not a good solution - Meticulous, ongoing attention is necessary to connections - Short, heavy gauge, and clean... Good luck. -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
|
In reply to this post by Hasan A. Khan
Hi Hasan,
I'm not sure I understand - when you say "discharged to about 80% of full charge" do you mean discharged from 100% (fully charged) to 80%, or do you mean from 100% to 20%? For example, on a 10 amp-hour battery, do you mean you are going to discharge out 8 amp-hours or 2 amp-hours? If you mean only discharging 20% depth of discharge (from 100% to 80% state of charge), then I think it is likely that an automotive battery would last almost two years. If you mean discharged 80% depth of discharge (100% to 20% state of charge) then no, they would not last very long at all. Maybe you explained this already and I missed it but why are you going to have such discharges on your UPS twice per week? As for the possibility of 220V on the battery terminals, I am not familiar with typical UPS design, but it is entirely possible that, to save money and weight, an auto-transformer or simple inductor was used instead of a fully-isolated transformer. Sean On Sat, May 2, 2009 at 3:06 PM, Hasan A. Khan <[hidden email]> wrote: > Thanks for everyone for their help! > My main concern was if the UPS's would work fine with wet cell batteries > and according to you guys, it will. So I am mostly happy. The concern > about deep cycle issues is still there since the batteries will be > discharged to about 80% of full charge atleast twice a weak. Given that > the batteries are well taken care of otherwise, will they last two years > with that frequency of deep discharge? > > Also I was not aware of the fact that 220V can appear on the battery > terminals. I don't understand how that can happen. I'd like to look at > some basic UPS circuits that will show it. Any pointers welcome. I > thought some sine/square wave is pumped into a step-up transformer with > input and output being isolated by the transformer. So how does high > voltage appear at the battery terminals? > > Thanks again. > > -Hasan > > -- > http://www.piclist.com PIC/SX FAQ & list archive > View/change your membership options at > http://mailman.mit.edu/mailman/listinfo/piclist > -- http://www.piclist.com PIC/SX FAQ & list archive View/change your membership options at http://mailman.mit.edu/mailman/listinfo/piclist |
| Powered by Nabble | Edit this page |